CoronaRaptor
FRF Addict
What you are not grasping (you're not alone here), is that just because there is a 20 amp fuse present, most people think the circuit will protect up to 20 amps, but that is not how it operates, this is the MAXIMUM amperage this circuit can handle. What this means is, if you have a 5amp light on this circuit, you need to protect it with a 5-6 amp fuse. You can leave the 20 amp fuse in the factory location, but you need to protect your circuit with a 5-6 amp fuse as well. What will happen, if you don't add this additional fuse is: lets say your lights short out and would normally trip at 5 amps, but with a 20 amp circuit (fuse), the fuse won't blow and then the circuit overheats ( highly possible) and melts the wiring.I suppose I am having trouble grasping the 80% rule for a circuit.
Take a circuit fused for a certain amount, say 20 amps. If you put a load on it that exceeds the 20 amps will the fuse not blow and protect the circuit? That is assuming the fuse was appropriately selected for the gauge of wire and the length of wire.
Does the issue turn into the fact that it may not present a load high enough to blow the fuse but will generate too much heat to cause an issue? But then again isn’t heat a result of current?
I guess my question is that shouldn’t the fuse on the factory upfitters be sized appropriately to protect the circuit despite whatever load the circuit may see?
Is the 80% more so that you don’t blow a fuse during normal operation rather than for protecting the circuit?